Copper 'earth' rod deep in the ground?

Recommended Posts

I'm having a so-called 'experienced' electric guy come soon to fix a few lights. 

 

Last yr on the ground floor of our newly renovated building we had a different electrician put in a new large elec box with proper grounding (so he says). He showed me where they put the copper rod with concrete over the top now. He was the same guy who did the wiring on a shower where I was subsequently feeling minor electric shocks when touching the metal tap. This issue has since been resolved. But now I want to dig up the concrete and check if the copper rod thing is done correctly. If not all it represents is 'fake safety'. 

 

Thus, my question is...

1. what are we looking for once the concrete is dug up. How deep should it be? Should it be covered in soil?

2. What am I looking for to see if it is actually fake safety?

 

thanks

Share this post


Link to post
Share on other sites
17 minutes ago, davidst01 said:

1. what are we looking for once the concrete is dug up. How deep should it be? Should it be covered in soil?

yes it should be driven into the earth (soil). two meters is typical but some are 3 meters. It should not be encased in concrete, it can be covered at the top with concrete.  

Share this post


Link to post
Share on other sites
29 minutes ago, davidst01 said:

1. what are we looking for once the concrete is dug up. How deep should it be? Should it be covered in soil?

The important point is that the soil must be constantly damp, if the earth is dry as a bone then it's in the wrong location.

  • Thanks 1

Share this post


Link to post
Share on other sites

Rather than dig everything up (you really can't tell much just by looking), find a sparks with a proper earth resistance tester and test what you have, it could be just fine.

 

Otherwise just bash in a second rod >2.4m long and wire it together with the existing rod (I would wire it to the board itself as if there was no existing rod). In reality this is likely the cheapest and easiest solution.

 

  • Thanks 1

Share this post


Link to post
Share on other sites
1 hour ago, Crossy said:

Rather than dig everything up (you really can't tell much just by looking), find a sparks with a proper earth resistance tester and test what you have, it could be just fine.

 

Otherwise just bash in a second rod >2.4m long and wire it together with the existing rod (I would wire it to the board itself as if there was no existing rod). In reality this is likely the cheapest and easiest solution.

 

Are you referring to one of these:

https://www.lazada.co.th/products/uni-t-ut501a-1000v-insulation-earth-ground-resistance-multimeter-voltmeter-tester-i331300834-s636756198.html?spm=a2o4m.searchlist.list.13.3340d1c0c8H0Xj&search=1

 

He pulled out a small device and when touching a wire it showed the voltage. Can that be used on the copper rod?

Share this post


Link to post
Share on other sites
1 hour ago, davidst01 said:

Are you referring to one of these:

https://www.lazada.co.th/products/uni-t-ut501a-1000v-insulation-earth-ground-resistance-multimeter-voltmeter-tester-i331300834-s636756198.html?spm=a2o4m.searchlist.list.13.3340d1c0c8H0Xj&search=1

 

He pulled out a small device and when touching a wire it showed the voltage. Can that be used on the copper rod?

 

No that Lazada unit is an insulation tester. The small device is some sort of voltage tester, not really suitable for checking an earth.

 

You or your man need one of these (and the knowledge of how to use it) https://www.lazada.co.th/products/vc4105a-digital-earth-ground-resistance-tester-meter-lcd-0012000-ac200v-i317488457-s596860968.html

 

Just banging in another rod would be a lot cheaper.

Share this post


Link to post
Share on other sites

As Crossy says... bang another rod in the ground.  Ideally drill a hole, confirm the ground is moist, and then bang the rod in.  Don’t put it in the same general vicinity as the original, and it will only improve things.  

Share this post


Link to post
Share on other sites
21 hours ago, Crossy said:

Rather than dig everything up (you really can't tell much just by looking), find a sparks with a proper earth resistance tester and test what you have, it could be just fine.

 

Otherwise just bash in a second rod >2.4m long and wire it together with the existing rod (I would wire it to the board itself as if there was no existing rod). In reality this is likely the cheapest and easiest solution.

 

Not that I doubt you Crossy, but why does the rod need to be more than 2.4metres?

 

 

Share this post


Link to post
Share on other sites
15 minutes ago, faraday said:

Not that I doubt you Crossy, but why does the rod need to be more than 2.4metres?

 

The oracles of dirt say so and the gurus of electric code obey.

  • Like 1
  • Thanks 1

Share this post


Link to post
Share on other sites
25 minutes ago, faraday said:

Not that I doubt you Crossy, but why does the rod need to be more than 2.4metres?

 

PEA / MEA regulations.

 

It likely doesn't need to be that deep to give an acceptable ground resistance but the code here is prescriptive like the NEC "do it like this and it's to code" rather than proscriptive like BS7671 "this is what you need to achieve, as the designer you decide how to achieve it".

  • Thanks 1

Share this post


Link to post
Share on other sites
On 7/24/2019 at 4:37 PM, Crossy said:

 

No that Lazada unit is an insulation tester. The small device is some sort of voltage tester, not really suitable for checking an earth.

 

You or your man need one of these (and the knowledge of how to use it) https://www.lazada.co.th/products/vc4105a-digital-earth-ground-resistance-tester-meter-lcd-0012000-ac200v-i317488457-s596860968.html

 

Just banging in another rod would be a lot cheaper.

hi, My update is that our electrician came around today to check things. I told him I wanted to check the copper rod and he used the drill to remove the top surface of the concrete. He didnt have a proper digital device as per your link above. But he did have a lightbulb with 2 wires attached. He stuck one end in the electric extension cord that was plugged into the drill. He touched the other wire from the bulb to the top of the copper rod thing. The light on the bulb flickered a little and then we heard the power cut out inside with a few beeping noises. He said that this test confirms the earth rod / grounding is working. Is this a valid test. Is he correct?

 

thanks so much

Share this post


Link to post
Share on other sites
9 hours ago, davidst01 said:

Is this a valid test.

 

Sort of. It could be a valid test of the rod, but it doesn't verify that the rod is actually connected to the board, a screwdriver stuck in the lawn would have done the same.

 

He should have disconnected the rod from the rest of the system at the board. Bet he didn't (he could have tested the rod from the other end of the cable then).

 

What device tripped and beeped?

 

I must admit I'm a bit confused as to exactly what you have in your building by way of actual distribution boards, breakers etc. It would be really useful if you could post photos of all of your electrical installation so we can work out what's going on.

 

 

 

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

  • Recently Browsing   0 members

    No registered users viewing this page.

×
×
  • Create New...