cable big enough for a concrete mixer ?

Recommended Posts

Hello !

 

From a neighbour land, I will use a cable (2 X 1 sq.mm) to power some tools while I am building a shelter. I think the most powerful will be a concrete mixer (170 Liters, 1000 Watts).

Would the cable suitable for such device? what about if I connect in the same time a electric drill, or grinder (about 500 watts).

Thanks to take time to answer 🙂

 

Share this post


Link to post
Share on other sites
3 minutes ago, thing31 said:

From a neighbour land, I will use a cable (2 X 1 sq.mm) to power some tools while I am building a shelter. I think the most powerful will be a concrete mixer (170 Liters, 1000 Watts).

Would the cable suitable for such device? what about if I connect in the same time a electric drill, or grinder (about 500 watts).

It isn’t suitable for running any power tools.
 

You haven’t given a distance that you are planning to run the extension. 

 

Most would not consider using anything less than 2 X 2.5mm2  

  • Like 1

Share this post


Link to post
Share on other sites

Well... actually it should be OK.  Most 20m wheel extensions are 1.5mm² (like mine) and I've had no issues running power tools with it.  Even my welder.  If you will be extending 50m or more, you really should go up to 2.5mm².  Try to run just one tool at a time.

 

Oh, I just noticed the OP said 1mm².  Yeah - need at least 1.5mm².

Edited by bankruatsteve

Share this post


Link to post
Share on other sites

Hello !

 

Thanks for your answers. Actually the 'extension' would be quite long, about 80-100m.

So, If I understand correctly, I  should buy at least 2.5 mm2 because of this long distance, either I use one or several tools, right ?

Share this post


Link to post
Share on other sites

Can you put in a construction supply meter to your land and run power off that?

 

Cheers

  • Like 1

Share this post


Link to post
Share on other sites
2 hours ago, thing31 said:

Hello !

 

Thanks for your answers. Actually the 'extension' would be quite long, about 80-100m.

So, If I understand correctly, I  should buy at least 2.5 mm2 because of this long distance, either I use one or several tools, right ?

2.5mm2 is what we used over a similar distance when building and it was okay even with a couple of welders and some other things plugged in.

 

Best is the multi strand cable but we actually used single core (twin and earth) and it was OK

Share this post


Link to post
Share on other sites

100m is a pretty long "extension lead" 🙂

 

If your tools pull a reasonable 10A or so then 100m of 2.5 is going to drop your supply by about 16V from whatever it was at the feed end. That's about 8% of 220V so you should be fine.

 

Watch how you run the cable as it's pretty easy to damage if run over regularly by vehicles.

 

The suggestion above of a "construction" supply is a good one if there is grid power nearby, you'll pay 8 Baht per unit but it does mean that you will have power to the place when finished.

 

Share this post


Link to post
Share on other sites
2 hours ago, Crossy said:

100m is a pretty long "extension lead" 🙂

 

If your tools pull a reasonable 10A or so then 100m of 2.5 is going to drop your supply by about 16V from whatever it was at the feed end. That's about 8% of 220V so you should be fine.

 

Watch how you run the cable as it's pretty easy to damage if run over regularly by vehicles.

 

The suggestion above of a "construction" supply is a good one if there is grid power nearby, you'll pay 8 Baht per unit but it does mean that you will have power to the place when finished.

 

What we actually did was to have a  "construction" supply as a backup to the 100 metre extension run from my neighbours meter. This meant that we mostly used the cheaper power (the cost was that we paid her bill so she got free power while we built). We had a small construction supply bill and were ready to swap to our own meter. It was certainly cheaper (including the cost of the extension) and gave an available 20A+ supply, and didn’t need to wait for the PEA to install the construction meter.

Edited by sometimewoodworker
  • Like 1

Share this post


Link to post
Share on other sites

I would just go for a portable generator... but that is me.  Depends entirely how long you need the temporary supply.

Share this post


Link to post
Share on other sites

Thanks everyone,

Yes, I will buy a 2.5 mm2 cable, it looks the best option in my case 🙂

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

  • Recently Browsing   0 members

    No registered users viewing this page.

×
×
  • Create New...