SAFE-T-CUT TRIPPING DAILY

Recommended Posts

This single 3 b/r single story house was built 30 years ago. It has a 15/45 meter dated 2007 and is protected by a Safe-T-Cut 10 slot 50 Amp. February we added a 12K BTU a/c in spare bedroom for a guest. We also have 2 other a/c's - 18K and 12K plus 3500 shower heater, Mits 250 watt water pump, plus microwave, rice cooker, pc. tv's etc.

 

No problem until 2 weeks ago and the hot weather. All 3 a/c run 24/7 along with 4 ceiling fans with no problem except if ANYTHING else like the water pump water heater or microwave is turned on the main breaker trips. I tried changing the RCBO dial from 20 amps to 30 amps but makes no difference. Also it seems that in the afternoon the voltage drops as our fans seem to slow down but a/c keep running.

 

The local sparky suggested changing meters but I think that he may think we have a 5/15 meter as do most of the village. He also suggested replacing all of the wiring but hate to do that if that is not going to help this problem. We have dad an occasional wiring problem in the past but it then only tripped the single breaker and not the main breaker and was easily resolved.

 

Any suggestions.

 

 

Share this post


Link to post
Share on other sites

Doesn't sound like an earth-leakage issue.

 

With everything running it's probable the breaker is popping not because of an earth-to-ground fault but a main circuit overheat condition. It could be the main breaker is fatigued and hasn't held its ampere rating.

 

An Ampere Clamp meter put on one of the mains incomers could tell you what your actual draw it when everything is on. Or, if one was not available, do it by guestimate by adding the max value ampere label ratings of all the devices that are drawing power when it trips the breaker.

 

The third option is to blindly replace either the breaker or the entire consumer unit.

If you're over the 50 Amp limit you might want to think about dividing the house circuits among two separate consumer units, or see if 3-phase is available from the utility and go with a 3-phase consumer unit. 

  • Like 1

Share this post


Link to post
Share on other sites
2 hours ago, impulse said:

My first recommendation would be to get an amp clamp to see exactly what the load is.  I'm also a fan of USB enabled multi-meters that record the voltage over time.  That way, you can see what's happening instead of guessing.  Here's the output from a Uni-T 71E, showing what I mean.  It can also be equipped with an amp clamp and record amperage to show exactly what's happening.  Not cheap, but a lot cheaper than having someone guess wrong and do a lot of futile work.

 

If I were a betting man, I'd bet you're getting a voltage sag that's causing your motors to pull higher amps, and when you get the inrush current from one more motor, it trips the breaker.

 

image.png.fa0f4a17938fdea879f863f7e4ead74b.png

TJ Voltage 180820.pdf 47.24 kB · 1 download

I guess first step is to get an amp clamp meter. Just check with Lazada and have from very cheap to over 1500 baht.  But I am pretty sure that there is some voltage drop in the afternoon because my UPS on the PC will switch to the yellow indicator light for a minute or 2. Also the whole village electricity will go off for 30 minutes to an hour during the day.

 

We built the house in 1992 and I am pretty sure that we started off with a 5/15 meter. Sometime later it was changed to 15/45 without my knowledge. Also the cable run is approx 60 meters from meter to back of house. In the last few years that have replaced the power poles with taller ones and if I connected the meter cable thru the front of the house it would probable shorten the distance to about 30 meters. Also I am certain that the meter to house cables are the original size from 1992.

 

Will report back after I get results from amp clamp meter.

 

Thanks all

  • Like 1

Share this post


Link to post
Share on other sites

Some rough calculation :

12K BTU a/c            1200
18K and                1600
12K plus             1200
3500 shower heater,        3500
 Mits 250 watt water pump,     250
 plus microwave,         2000
rice cooker,              600
pc.                  350
tv's etc.              150 + 150

 

                11000
            11Kw / 230V = 47.8A
            190V = 58A

 

Everything on at the same time, showering, cooling the room cooking rice while the porridge heating up in the microwave for the guests in their just turned on air-conditioned rooms and the wife taking a long hot shower with the taps all open on the second floor.

Well , then you are right hitting the 50amp breaker. 

It could be worn and tripping below the rating.

You can try to replace it for a 63 Amp type.

 

About the wiring, it would be useful to check the wiring from the mains to the breakers and to the one that use the most power. High amp gives resistance on too thin wires and that will drop the voltage which then cause the current go up. This is important with the incoming wires.

 

 

  • Like 1

Share this post


Link to post
Share on other sites
11 minutes ago, livram said:

I guess first step is to get an amp clamp meter. Just check with Lazada and have from very cheap to over 1500 baht.  But I am pretty sure that there is some voltage drop in the afternoon because my UPS on the PC will switch to the yellow indicator light for a minute or 2. Also the whole village electricity will go off for 30 minutes to an hour during the day.

 

We built the house in 1992 and I am pretty sure that we started off with a 5/15 meter. Sometime later it was changed to 15/45 without my knowledge. Also the cable run is approx 60 meters from meter to back of house. In the last few years that have replaced the power poles with taller ones and if I connected the meter cable thru the front of the house it would probable shorten the distance to about 30 meters. Also I am certain that the meter to house cables are the original size from 1992.

 

Will report back after I get results from amp clamp meter.

 

Thanks all

As well as checking the amp draw when you have all the power hungry items running I would check the voltage at your main board and at the meter. If you are getting a significant drop between the 2 then you need to look at the cables from the meter to your house, as they would be undersized, so shortening them or doubling them would help

 

 

4 hours ago, livram said:

I tried changing the RCBO dial from 20 amps to 30 amps but makes no difference.

What you changed was not from 20 Amps to 30 Amps but the trip current from 20 milliamperes to 30 milliamperes.

 

So it obviously would not have made a difference to the overload trips that you are getting.

 

the Amp rating of the Safe-T-Cut at 50A should probably be enough  It could be that it is fatigued and failing if it’s as old as the house.

 

however if there’s no voltage drop, the Safe-T-Cut is in good condition and the power draw is exceeding the safety factor then I would ask to upgrade your supply to a 30/100 meter.

 

your items should be ok on the current supply unless the voltage is dropping very very low, which it certainly could be. Then talking to the PEA to try to get them to fix that would be worth trying 

  • Like 1

Share this post


Link to post
Share on other sites
9 hours ago, Metropolitian said:

Some rough calculation :

12K BTU a/c            1200
18K and                1600
12K plus             1200
3500 shower heater,        3500
 Mits 250 watt water pump,     250
 plus microwave,         2000
rice cooker,              600
pc.                  350
tv's etc.              150 + 150

 

                11000
            11Kw / 230V = 47.8A
            190V = 58A

 

Everything on at the same time, showering, cooling the room cooking rice while the porridge heating up in the microwave for the guests in their just turned on air-conditioned rooms and the wife taking a long hot shower with the taps all open on the second floor.

Well , then you are right hitting the 50amp breaker. 

It could be worn and tripping below the rating.

You can try to replace it for a 63 Amp type.

 

About the wiring, it would be useful to check the wiring from the mains to the breakers and to the one that use the most power. High amp gives resistance on too thin wires and that will drop the voltage which then cause the current go up. This is important with the incoming wires.

 

 

Thanks for all of the good advice. The Safe-T-Cut 50A is only 2 years old but I will take some measurements and have all the wiring checked. 

Share this post


Link to post
Share on other sites

All good stuff above, definitely time to make some voltage and current measurements.

 

One further question, are your aircons regular or inverter types?

 

Share this post


Link to post
Share on other sites
9 minutes ago, Crossy said:

All good stuff above, definitely time to make some voltage and current measurements.

 

One further question, are your aircons regular or inverter types?

 

A/C are regular type. Also I never mentioned that the Safe-T-Cut box is not grounded. The shower heater is grounded and when water pump was replaced 5 months ago the new model Mitsu* e255 had no way to ground it although the older version did have a ground wire.

Share this post


Link to post
Share on other sites

Without a meter there's not a lot you can do really.

 

You could try estimating the current by counting the revolutions of your meter disc in one minute and working backwards from that (you'll have to assume a 220V supply).

 

If you turn off one of the aircons can you then use other appliances OK?

Share this post


Link to post
Share on other sites
Posted (edited)

Someone will shoot me down I know but...

Once a breaker has tripped , with each subsequent trip it becomes more susceptible to tripping.

 

The first question to be asked when troubleshooting is: What has changed? In the OP case 

Quote

February we added a 12K BTU a/c in spare bedroom for a guest. 

 

Depending on the OP's location SafeT-Cut will come and check out the unit. That will involve them spotting the obvious no ground but...

 

Edited by VocalNeal

Share this post


Link to post
Share on other sites
Posted (edited)
8 minutes ago, Crossy said:

Without a meter there's not a lot you can do really.

 

You could try estimating the current by counting the revolutions of your meter disc in one minute and working backwards from that (you'll have to assume a 220V supply).

 

If you turn off one of the aircons can you then use other appliances OK?

Yes, the problem only occurs when ALL 3 A/C are turned on, then when water pump, heater, or microwave are turned on the whole system shuts off.

 

Right now when I want to use another appliance I turn off my a/c 18K and no problems at all.

Edited by Crossy
ON substituted for OFF after discussion with poster

Share this post


Link to post
Share on other sites

It does sound like over-current although I am surprised that it's tripping with that load. You could well have a low supply voltage too.

 

Time for some measurements.

 

How to proceed then will depend upon what you find.

Share this post


Link to post
Share on other sites
6 minutes ago, livram said:

Right now when I want to use another appliance I turn off my a/c 18K and no problems at all.

So indeed appears a trip due to use of excessive current.  Do you have a main breaker or is that Safe-T-Cut acting alone?  You might have to remove one of the air conditioners from the Safe-T-Cut protection if you have two breakers.

Share this post


Link to post
Share on other sites

Yeah ^^^.

 

Can you post some photos of what you have, Safe-T-Cut make a number of different devices.

Share this post


Link to post
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now

  • Recently Browsing   0 members

    No registered users viewing this page.

×
×
  • Create New...