I'd be tempted to pull those two whites from the ground bar and see if anything stops working (coz it's getting a return path via the ground).

 

In our old condo ALL the aircon was connected with the neutral feeds on the ground bar, supply was TN-S so it worked just fine until I wanted to install an RCBO.

 

  • Like 2
Link to comment
Share on other sites

8 minutes ago, Crossy said:

You absolutely need a KNOWN reference, you cannot rely on ANYTHING in the box for now. Bang that big driver into the lawn and water it if it's a bit dry.

 

 

I did notice two white wires on the ground bus.

I am not an Electrician but a Electo-mechanical repairman. So in 42 years of work when I measured incoming power to my machines if ir wasn't right I had the customer get their electrician to rectify the problem.  So my experience is not as an Electrician. different skill set 

  • Like 1
Link to comment
Share on other sites

Just now, Jack 0009 said:

I did notice two white wires on the ground bus.

I am not an Electrician but a Electo-mechanical repairman. So in 42 years of work when I measured incoming power to my machines if ir wasn't right I had the customer get their electrician to rectify the problem.  So my experience is not as an Electrician. different skill set 

I agree with you must know reference

  • Like 1
Link to comment
Share on other sites

2 minutes ago, Jack 0009 said:

I did notice two white wires on the ground bus.

I am not an Electrician but a Electo-mechanical repairman. So in 42 years of work when I measured incoming power to my machines if ir wasn't right I had the customer get their electrician to rectify the problem.  So my experience is not as an Electrician. different skill set 

 

Still likely better than a Thai domestic sparks ???? 

 

Thailand has many very good electricians, but most of them are earning $$$ on the mega-projects or O&G.

  • Like 2
Link to comment
Share on other sites

15 minutes ago, Crossy said:

I'd be tempted to pull those two whites from the ground bar and see if anything stops working (coz it's getting a return path via the ground).

 

In our old condo ALL the aircon was connected with the neutral feeds on the ground bar, supply was TN-S so it worked just fine until I wanted to install an RCBO.

 

another thing I did was measure between E and N then turn the individual breakers off one at a time.  generally had around 75 VAC but on one of the breakers that voltage dropped to around 50 VAC 

Link to comment
Share on other sites

2 hours ago, Crossy said:

I'd be tempted to pull those two whites from the ground bar and see if anything stops working (coz it's getting a return path via the ground).

 

In our old condo ALL the aircon was connected with the neutral feeds on the ground bar, supply was TN-S so it worked just fine until I wanted to install an RCBO.

 

Indeed it appears someone attached neutral wires to the ground bus at some point (probably did not see the 1/2/3 open slots on the neutral bar as above the "N").  Not sure where the Safe-t-cut is in system but if before panel a trip of that or main breaker should make panel safe to work on (but check everything with multimeter to be sure).  If these white lines are indeed neutrals something will stop working when detached and they can be attached to the neutral bar where they should be. (power off again of course).

Link to comment
Share on other sites

1 hour ago, bankruatsteve said:

With main breaker off, I would move those 2 (apparent neutral wires) from the ground bar to the neutral bar first.  That might be your issue.

 

Whilst it's not likely to introduce a hazard I'd really like to know what they are first. 

 

Disconnect them and see if anything stops working would be my first move.

 

  • Like 2
Link to comment
Share on other sites

36 minutes ago, Crossy said:

 

Whilst it's not likely to introduce a hazard I'd really like to know what they are first. 

 

Disconnect them and see if anything stops working would be my first move.

 

 

 

More importantly, check if the 75V between N - G goes away.

Link to comment
Share on other sites

9 minutes ago, 86Tiger said:

More importantly, check if the 75V between N - G goes away.

 

I've already set out in earlier posts what I would do to diagnose the issue based upon what our OP is reporting (tingles from earthed kit and an apparent 75V N-E). 

 

If our OP wishes to randomly add bits to his installation without actually diagnosing the issue it's entirely up to him.

 

Horses, water etc.

 

I still suspect a floating ground but ...

  • Like 2
Link to comment
Share on other sites

On 3/28/2021 at 9:19 AM, Crossy said:

Is that ground actually connected to the ground at the box and then the rod? A LOT of extension leads hve 3-pin plugs and outlets with 2 core cable!

Yes and a lot of circuits have earths that go to the earth bar in the consumer unit and no further ????.

  • Haha 1
Link to comment
Share on other sites

On 3/28/2021 at 3:21 PM, PMK said:

OK. I will do my own ground. I actually started to do that but backed off because of the other opinion.  I'm familiar with the ungrounded 3 pin extensions in Thailand. ????

 

 

 Do a PH , test on your soil . 

   Conductivity varies ,  on soils PH ..

    

Link to comment
Share on other sites

On 4/2/2021 at 6:07 AM, daveAustin said:

Likely unsound earth/awry neutral, though both of which would trigger rcd. As an aside, if you run a washing machine it'll induce emf on spin and bung it everywhere if no solid earth. Sorry, bruv, but your wiring sucks. ????

 

 Electro Motive Force .

  Ah, those were the days ..555

   

Link to comment
Share on other sites

On 3/30/2021 at 5:04 PM, Crossy said:

 

I've already set out in earlier posts what I would do to diagnose the issue based upon what our OP is reporting (tingles from earthed kit and an apparent 75V N-E). 

 

If our OP wishes to randomly add bits to his installation without actually diagnosing the issue it's entirely up to him.

 

Horses, water etc.

 

I still suspect a floating ground but ...

You are correct sir it was a floating ground. I went over to his house today and he hooked up a temporary ground. the voltages measured at nominal voltages and no more getting shocked of his Guitar. 50Hz hum on his amp is gone as well

  • Like 2
Link to comment
Share on other sites

Finally got a least a good temporary ground installed. No shocks, no weird noises from my guitar amp anymore. Less than 1 volt diff between earth and neutral now. I have an "electrician" - don't know yet if he deserves the title, coming up soon to run a proper new ground and give an opinion/explanation on those white wires going to the ground bus.  I'm not inclined to move them just to see what happens. ????

  • Like 1
Link to comment
Share on other sites

Create an account or sign in to comment

You need to be a member in order to leave a comment

Create an account

Sign up for a new account in our community. It's easy!

Register a new account

Sign in

Already have an account? Sign in here.

Sign In Now
  • Recently Browsing   0 members

    • No registered users viewing this page.




×
×
  • Create New...